What happens when there is much load on the inverter?
Share
Sign Up to our social questions and Answers Engine to ask questions, answer people’s questions, and connect with other people.
Login to our social questions & Answers Engine to ask questions answer people’s questions & connect with other people.
Lost your password? Please enter your email address. You will receive a link and will create a new password via email.
Please briefly explain why you feel this question should be reported.
Please briefly explain why you feel this answer should be reported.
Please briefly explain why you feel this user should be reported.
Most UPS inverters come with an overload capability. Usually two overload settings are provided by the manufacturer.
For example, there might be a 125% overload withstand capability of 60s and a 150% overload withstand capability of, say, 6 seconds.
In case current exceeds the overload capability, the UPS goes in ‘constant current’ mode wherein the current is prevented from increasing any further but at expense of rapidly falling output voltage.
In such a case, if current doesn’t fry the electronic components, the UPS will trip on overcurrent or low output voltage fault.